fas 0 Posted July 29, 2008 All of my cameras in this particular system pull between 500 and 1000 milliamps. I am looking at a power supply that has these specs: Output: 24V AC/ 16 Output Supply Current: 5amp Max Amp: 1.1 Amp/Channel Does that mean each of the 16 channels will support a camera pulling 1 amp? Share this post Link to post Share on other sites
vin2install 0 Posted July 29, 2008 That unit supplies a total of 5 A. So with all 16 channels the load cannot total more than 5A. But you can have 1.1A max on one channel but all other channels must add up to 3.9A max. Share this post Link to post Share on other sites
survtech 0 Posted July 29, 2008 To add to that, I wouldn't recommend connecting a camera that is rated to draw 1000ma to a power supply that is rated at 1.1 amp (1100ma) maximum per channel. That is asking for trouble! Common practice is to never exceed 80% of maximum rating; therefore each channel should be rated at least 1.25 amps (1250ma) and the supply as a whole should be rated at least 1.25 times the total current draw. One question: Few 24VAC cameras are rated in milliamps and relatively few cameras other than PTZ's or IR cameras with built-in IR LED's draw that much power. Most are rated in VA (volt-amps), which is voltage times current. Usually only DC cameras are rated in ma. Are you certain your cameras operate on 24VAC? Share this post Link to post Share on other sites
fas 0 Posted July 29, 2008 Here is the camera: http://nuvico.com/downloadfile.htm?id=132 Share this post Link to post Share on other sites
survtech 0 Posted July 29, 2008 You might want to double-check the specs with Nuvico. First, there are no regulated 24VAC power supplies that I know of. Second, if the camera draws 500ma at 12VDC, that would be 6VA (approximately the same as 6 watts) (0.5 x 12). If it still draws 500ma at 24VAC, that would be 12VA (approximately the same as 12 watts). So the big question is what happens to the extra 6VA (watts)? It can't just disappear into thin air so something has to dissipate it. While 6 watts doesn't sound like an awful lot when compared to a 100 watt light bulb or a 1,500 watt space heater, it is a lot when it comes to electronic equipment. If that power is not used by the electronics, it has to be dissipated as heat. 6 watts is a lot of heat to dissipate, especially in a camera. Share this post Link to post Share on other sites
ak357 0 Posted July 30, 2008 You might want to double-check the specs with Nuvico. First, there are no regulated 24VAC power supplies that I know of. Second, if the camera draws 500ma at 12VDC, that would be 6VA (approximately the same as 6 watts) (0.5 x 12). If it still draws 500ma at 24VAC, that would be 12VA (approximately the same as 12 watts). So the big question is what happens to the extra 6VA (watts)? It can't just disappear into thin air so something has to dissipate it. While 6 watts doesn't sound like an awful lot when compared to a 100 watt light bulb or a 1,500 watt space heater, it is a lot when it comes to electronic equipment. If that power is not used by the electronics, it has to be dissipated as heat. 6 watts is a lot of heat to dissipate, especially in a camera. On 24 V side it does not take 500 ma Share this post Link to post Share on other sites
fas 0 Posted July 30, 2008 Do you know what it takes on the 24v side? Share this post Link to post Share on other sites
fas 0 Posted July 30, 2008 Just confirmed with Nuvico it takes 500mA on the 24V side as well. Share this post Link to post Share on other sites
survtech 0 Posted July 30, 2008 Well, 500ma is 1/2 amp. Therefore, each output of the power supply should be fused at 1 amp. If you have 16 of those cameras connected to a single power supply, the supply should be rated at 8 amps total plus at least 20% headroom or 10 amps total. You can get a power supply rated higher than that, but no lower. Share this post Link to post Share on other sites
fas 0 Posted July 30, 2008 I am getting a 24vac central power supply rated at 10 amps. Share this post Link to post Share on other sites
ak357 0 Posted July 30, 2008 Just confirmed with Nuvico it takes 500mA on the 24V side as well. Well, here we go just for fun measured DC and AC current for CNB dual voltage D2315 camera 12V---.26A ~ 3wt 24V---.13A ~ 3wt not to be mean but... plz call back Nuvico tech support and ask if anybody ever measure current and at the same time ask if anybody remember Ohm's law u might be surprise with answer Share this post Link to post Share on other sites
survtech 0 Posted July 31, 2008 Just confirmed with Nuvico it takes 500mA on the 24V side as well. Well, here we go just for fun measured DC and AC current for CNB dual voltage D2315 camera 12V---.26A ~ 3wt 24V---.13A ~ 3wt not to be mean but... plz call back Nuvico tech support and ask if anybody ever measure current and at the same time ask if anybody remember Ohm's law u might be surprise with answer Bravo!!! Unless they internally drop the voltage from 24V to 12V by dissipating it as heat (I doubt they would use a DC-DC inverter due to cost), the power drawn by the camera should be the same. If the voltage doubles (12V to 24V) the current would be cut in half (500ma to 250ma). Then again, it doesn't hurt to over-rate the power supply. Share this post Link to post Share on other sites