Which alarm sensors?

Recommended Posts


Any dry-contact relay should do the trick. All the inputs are typically looking for is a change of state. By default it's probably set up for normally-open contacts - shorting between the two input pins would trigger it. You can probably configure it to look for normally-closed input as well.

Share this post


Link to post
Share on other sites

I thought this too, but any option I set ("high" or "low") for the inputs, connecting them to GND does not have any effect.

That's why I'm asking if I have to apply some voltage.

Share this post


Link to post
Share on other sites

The manual mentions a setting for low-voltage and high-voltage. Perhaps there was an error in the translation and they meant something like 0V and +5V. Check the settings, and you might try pulling up with a resister.

 

Best,

Christopher

Share this post


Link to post
Share on other sites

I did additional tests: alarm is triggered if input is set to HIGH and connected to nothing; connecting it to GND stops the alarm.

Share this post


Link to post
Share on other sites
I did additional tests: alarm is triggered if input is set to HIGH and connected to nothing; connecting it to GND stops the alarm.

 

Yes, that's what I would have expected after reading the manual. There is a setting that allows you to either pull up or pull down to trigger the alarm.

 

Best,

Christopher

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

×