johngaiger 0 Posted February 21, 2008 I have Dedicated micros DS2 (old model) and have been trying to get a jvc tk-676 to run on it. I connected the jvc rx- to pin 5 and rx+ to pin 3 on the 9 pin dtype connection. The jvc is set to simplex mode and point to point. The camera self tests and displays a picture but I have no control. I set the DS2 telemetry to JVC. I tried the same with a VCL orbiter gold lite. that would rotate 180 every time i moved the joystick foreward but thats all. can anyone help? regards John Share this post Link to post Share on other sites
crirvine 0 Posted February 21, 2008 Can you set the camera and dvr to PELCO D ? With baud rate 9600 8 none and 1. You should see about 3.5 to 5.0 volts dc on the 485 + - ports at the dvr. That is a much better standard for me. Share this post Link to post Share on other sites